          Is there information available on what a resident may need to know in regards to Carbon Monoxide alarms, Smoke Dectors, and Low Voltage Fire Alarm systems?

TOWNSHIP OF MAHWAH FIRE PREVENTION

 

CARBON MONOXIDE ALARMS – WHAT YOU NEED TO KNOW

 

On April 7, 2003 New Jersey adopted regulations for the installation of Carbon Monoxide Alarms in the vicinity of all sleeping areas in buildings that contain fuel burning appliances or have an attached garage.

 

Carbon Monoxide Alarms should be installed with 10 feet of any sleeping areas so they will be audible in each bedroom.  Multiple Carbon Monoxide Alarms may be necessary to accomplish this requirement.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement.

 

Carbon Monoxide Alarms may be battery type, AC plug-in type or part of the building alarm system.  All devices shall be listed and installed as per the manufacturers’ instructions.  As of Jan 1, 2019, 10 year sealed battery detectors will be required.

 

CO DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED

 

SMOKE DETECTORS – WHAT YOU NEED TO KNOW

 

Smoke detector requirements vary because of code changes adopted over the past years.  At a minimum, homes built prior to January 1977 require battery detectors to be installed.  One on each level and outside of each sleeping area usually with 10 feet of any bedroom doors.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement.

 

As of Jan 1, 2019, 10 year sealed battery detectors will be required

 

ALL INSTALLED SYSTEMS MUST BE MAINTAINED AT ALL TIMES (IFC 907.1.11.2).

 

Any building constructed after January 1977 needs to meet the requirements of the code at the time the building was constructed.  If the code only required hard wired smoke detectors on one or two floors, hardwired detectors need to be installed on each floor.  However, A/C-powered single or multiple-station smoke alarms installed as part of the original construction or rehabilitation project shall not be replaced with battery-powered smoke alarms.  Click here to view Samples of Hard-wired on the left, battery in the middle, and CO on the right.

 

SMOKE DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED

 

LOW VOLTAGE FIRE ALARM SYSTEMS – WHAT YOU NEED TO KNOW
 

Low Voltage Fire Alarm Systems and any Fire Alarms that are monitored by a central notification station must be maintained in accordance with NFPA 72 and the homeowner must provide a system test report at the time of inspection.  Failure to provide a system test report that shows no deficiencies will be cause for failure and a re-inspection will be needed.

 

Starting January 1, 2006, Mahwah Fire Prevention will begin enforcing the adopted State requirements (N.J.S.A. 52:27D-198.1) for fire extinguishers in one and two family dwellings along with smoke detectors and carbon monoxide detectors at the change of occupancy.

The requirements for extinguisher type and placement are as follows (N.J.A.C 5:70-4.19(e):

  1. At least one portable fire extinguisher shall be installed in all one and two family dwellings upon change of occupancy.

 

  1. The extinguisher shall be listed, labeled, charged and operable.

 

  1. The size shall be no smaller than 2A:10B:C, rated for residential use and weighs no more than 10lbs.

CLICK HER TO VIEW PHOTO

 

  1. The hangers or brackets supplied by the manufacturer must be used.

 

  1. The extinguisher must be within 10 feet of the kitchen and located in the path of egress.

 

  1. The top of the extinguisher must be no more than 5 feet above the floor.

 

  1. The extinguisher must be readily accessible location and not obstructed from view.

 

  1. The owner’s manual or written information regarding the operation shall be provided during the inspection

 

  1. The extinguisher shall be serviced and tagged within the past 12 months or the seller must have a receipt for a recently purchased extinguisher.

 



          What are the regulations for smoke detectors, carbon monoxide alarm and fire extinguishers?

TOWNSHIP OF MAHWAH FIRE PREVENTION

CARBON MONOXIDE ALARMS – WHAT YOU NEED TO KNOW

On April 7, 2003 New Jersey adopted regulations for the installation of Carbon Monoxide Alarms in the vicinity of all sleeping areas in buildings that contain fuel burning appliances or have an attached garage.

Carbon Monoxide Alarms should be installed with 10 feet of any sleeping areas so they will be audible in each bedroom.  Multiple Carbon Monoxide Alarms may be necessary to accomplish this requirement.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement.

Carbon Monoxide Alarms may be battery type, AC plug-in type or part of the building alarm system.  All devices shall be listed and installed as per the manufacturers’ instructions.

CO DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED

 

SMOKE DETECTORS – WHAT YOU NEED TO KNOW

Smoke detector requirements vary because of code changes adopted over the past years.  At a minimum, homes built prior to January 1977 require battery detectors to be installed.  One on each level and outside of each sleeping area usually with 10 feet of any bedroom doors.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement.  All installed systems must be maintained at all times (IFC 907.1.11.2).

Any building constructed after January 1977 needs to meet the requirements of the code at the time the building was constructed.  If the code only required hard wired smoke detectors on one or two floors, 10 year sealed battery detectors (as of Jan 1, 2019) or hardwired detectors need to be installed on each floor.  However, A/C-powered single or multiple-station smoke alarms installed as part of the original construction or rehabilitation project shall not be replaced with battery-powered smoke alarms.

SMOKE DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED

 

LOW VOLTAGE FIRE ALARM SYSTEMS – WHAT YOU NEED TO KNOW

Low Voltage Fire Alarm Systems and any Fire Alarms that are monitored by a central notification station must be maintained in accordance with NFPA 72 and the homeowner must provide a system test report at the time of inspection.  Failure to provide a system test report that shows no deficiencies will be cause for failure and a re-inspection will be needed.

Starting January 1, 2006, Mahwah Fire Prevention will begin enforcing the adopted State requirements (N.J.S.A. 52:27D-198.1) for fire extinguishers in one and two family dwellings along with smoke detectors and carbon monoxide detectors at the change of occupancy.

The requirements for extinguisher type and placement are as follows (N.J.A.C 5:70-4.19(e):

  1. At least one portable fire extinguisher shall be installed in all one and two family dwellings upon change of occupancy.

 

  1. The extinguisher shall be listed, labeled, charged and operable.

 

  1. The size shall be no smaller than 2A:10B:C, rated for residential use and weighs no more than 10lbs.

CLICK HERE TO VIEW PHOTO

  1. The hangers or brackets supplied by the manufacturer must be used.

 

  1. The extinguisher must be within 10 feet of the kitchen and located in the path of egress.

 

  1. The top of the extinguisher must be no more than 5 feet above the floor.

 

  1. The extinguisher must be readily accessible location and not obstructed from view.

 

  1. The owner’s manual or written information regarding the operation shall be provided during the inspection

 

  1. The extinguisher shall be serviced and tagged within the past 12 months or the seller must have a receipt for a recently purchased extinguisher.

 



          What you need to know about Carbon Monoxide Alarms

TOWNSHIP OF MAHWAH FIRE PREVENTION

CARBON MONOXIDE ALARMS – WHAT YOU NEED TO KNOW

On April 7, 2003 New Jersey adopted regulations for the installation of Carbon Monoxide Alarms in the vicinity of all sleeping areas in buildings that contain fuel burning appliances or have an attached garage.

Carbon Monoxide Alarms should be installed with 10 feet of any sleeping areas so they will be audible in each bedroom.  Multiple Carbon Monoxide Alarms may be necessary to accomplish this requirement.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement.

Carbon Monoxide Alarms may be battery type, AC plug-in type or part of the building alarm system.  All devices shall be listed and installed as per the manufacturers’ instructions.  As of Jan 1, 2019, 10 year sealed battery detectors will be required.

CO DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED



          What you need to know about Low Voltage Fire Alarm Systems

LOW VOLTAGE FIRE ALARM SYSTEMS – WHAT YOU NEED TO KNOW
 

Low Voltage Fire Alarm Systems and any Fire Alarms that are monitored by a central notification station must be maintained in accordance with NFPA 72 and the homeowner must provide a system test report at the time of inspection.  Failure to provide a system test report that shows no deficiencies will be cause for failure and a re-inspection will be needed.

 

 



          What you need to know about smoke detectors.

SMOKE DETECTORS – WHAT YOU NEED TO KNOW

Smoke detector requirements vary because of code changes adopted over the past years.  At a minimum, homes built prior to January 1977 require battery detectors to be installed.  One on each level and outside of each sleeping area usually with 10 feet of any bedroom doors.  The use of a combination Smoke and CO detector is allowed to fulfill the requirement. 

As of Jan 1, 2019, 10 year sealed battery detectors will be required

All installed systems must be maintained at all times (IFC 907.1.11.2).

Any building constructed after January 1977 needs to meet the requirements of the code at the time the building was constructed.  If the code only required hard wired smoke detectors on one or two floors, hardwired detectors need to be installed on each floor.  However, A/C-powered single or multiple-station smoke alarms installed as part of the original construction or rehabilitation project shall not be replaced with battery-powered smoke alarms.  Click here to view samples of Hard-wired  on the left, Battery in the middle and and CO on the right. 

                            

SMOKE DETECTORS 10 YEARS OLD OR OLDER MUST BE REPLACED

 



 



Access For All Commission | Home | General Information Section | About Mahwah | Calendar of Events | Employment Opportunities  | Helpful Links | Live Meetings Video | News & Announcements | Photo Journal | Elected Officials | Mayor's Online Office | Township Council | Boards, Commissions & Committees   | Government Representatives | Government | Bids, RFP's, RFQ's, Notice of Intent  | Community Emergency Response Team (CERT) | Contacts Directory | Departments | E-Mail Subscriptions | Emergency Services | Forms Center | Frequently Asked Questions | Meeting Agendas & Minutes | Municipal Code  | Senior Center | Township of Mahwah Police Department | SWIFT 911 Notification | Mahwah Museum | Mahwah Schools